Innoswitch EP isolation level
in the datasheet of InnoSwitch-EP is stated that this family meet reinforced isolation requirements.
Is it true according to IEC standard?
How can I access this compliance evidence/test certificate for the InnoSwitch-EP family?
Best Regrds
Michal
Hello Kazuya,
thank You for the answer, but I have another one - what about insulation level according to UL certification?
Has the InnoSwitch-EP UL certification for reinforced isolation level?
Best Regards
Michal
Hi Michal,
The product has been certified as single protection, non-optical isolator in UL. For your information, UL1577 standard does not have the option for reinforced insulation. A double insulation is considered the equivalent to reinforced insulation in the IEC standard world. This has nothing to do with double protection in UL1577.
Best regards,
Kazuya
Hi Kazuya,
thank You very much for all information.
Best regards
Michal
Hello Michal,
Thanks for reaching out.
You are correct. The InnoSwitch-EP family meets the Reinforced isolation according to the requirements of EN/IEC 62368-1 standard. Such approval was obtained from TUV Rheinland with certificate number R 72203545 (for EN certification) and US-TUVR-012323 (for IEC certification) for your reference and validation. However, we do not post these certificates in public for some reason. I hope that helps.
Best regards,
Kazuya
